Richard wrote:How do I connect that to my AC panel? Does my AC panel have a place for it? Do you have a product number? ...
You claim additional devices are not necessary for cable and telephone based on them being properly grounded. What is your answer to the home owner who has suffered damage via one of these lines yet the provider claims it is not their fault and the line was properly installed?
So many protectors install so many ways. All is well beyond the scope of this discussion. This is about what it must do - how it must connect. How to install it is unique to each selected protector, local electrical codes, what currently exists, what is needed to upgrade or install earthing, etc. None of that is difficult - just laborious.
An example (model CHSPMICRO) from Lowes:
http://www.lowes.com/lowes/lkn?action=p ... lpage=none
Another example from Lowes (model BRSURGECS) that mounts differently:
http://www.lowes.com/lowes/lkn?action=p ... lpage=none
One from Intermatic:
http://www.smarthome.com/4870.HTML
One from Leviton:
http://www.smarthome.com/4860.html
Delta LA302R:
http://www.deltala.com/prod01.htm#LA302R
Utilities are required by code to earth their wires (directly or via a protector). But remember the soundbyte? "A protector is only as effective as its earth ground". Who is responsible for providing that ground? Who must enhance that ground for surge protection? You. Or your hired agent (the electrician).
If you had damage, an investigation starts with what you are responsible for - earthing.
An example to learn from. A FL home was repeatedly struck on the side wall. They had lightning rods installed and earthed with an 8 foot ground rod. Lightning again struck the side wall. Lightning rods were only earthed in sand. Plumbing inside the wall was connected to deeper and more conductive limestone. And again, "a protector was only as effective as its earth ground".
If you had damage, well, how good is your earthing? Is it single point? Do all wires make short connections to those electrodes? Do those wires only meet at that single point ground? Follow the surge. What path did it take to earth?
One house had a 'whole house' protector. But lightning still traveled through the house. On the far side was a buried vein of graphite. Lightning was still seeking that better earth ground. Solution was to encircle the house with a buried ground loop. Now the surge need not pass through the house to be earthed by more conductive soil.
There is no 'magic box' solution in any of these stories. Solution is exactly what was the solution even 100 years ago. Earthing. In every case, effective protection is about earthing. And yet still so many want to buy a 'magic box' protector. Surges are earthed - either harmlessly without entering a building or destructively through household appliances. That energy must be dissipated somewhere. That current will increase voltage (destructively) as necessary to continue flowing. So we learn why human error permitted that surge damage.
Best evidence always is the dead bodies. What was a destructive path to earth? If you had surge damage, then use damage to learn of a mistake; that permitted damage to happen.
Cited were examples (Orange County FL fixed their earthing), IEEE Standard 142 quoted, how to connect low impedance to earth, numerous 'whole house' protectors from more responsible companies, standards that even require appliances to withstand 2000 and 15,000 volts, a Monster Cable $150 scam, US Air Force and Sun Microsystems demands for the same 'whole house' solution, protection even when 33,000 volts blew electric meters up to 30 feet from their pans, and how earthing must be installed or upgraded.
If damage happens, why was a single point earth ground not the best earth? Another quote from the NIST is blunt about this:
> A very important point to keep in mind is that your surge protector will work
> by diverting the surges to ground. The best surge protection in the world
> can be useless if grounding is not done properly.
If you had damage, something is wrong or insufficient with the earthing that you must provide. Unfortunately that is an art. Provided were underlying concepts and principles. The art is to learn from damage so as to correct an earthing mistake. The solution is to dissipate surges harmlessly in earth so that surge currents do not even enter the building. IOW a protector is only as effective as its earth ground.
Some suggestions may be found in a case study of earthing upgrades to a Nebraska radio station:
http://www.copper.org/applications/elec ... raska.html
Appreciate why they even upgraded the utility power transformer ground.